We need volunteers for the following: -Install PDU and wire up server and switch power cords -Install Akamai router (not yet arrived) -Power up servers and do any remaining initial provisioning (After IP connectivity is established) -Akamai built in Route Servers Please reply to the list so everyone knows what's going on. Thanks, Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
I am willing to help -----Original Message----- From: MICE Discuss [mailto:MICE-DISCUSS@LISTS.IPHOUSE.NET] On Behalf Of Jay Hanke Sent: Wednesday, September 28, 2011 9:37 AM To: MICE-DISCUSS@LISTS.IPHOUSE.NET Subject: [MICE-DISCUSS] Akamai Cluster Help We need volunteers for the following: -Install PDU and wire up server and switch power cords -Install Akamai router (not yet arrived) -Power up servers and do any remaining initial provisioning (After IP connectivity is established) -Akamai built in Route Servers Please reply to the list so everyone knows what's going on. Thanks, Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1 ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On Wed, Sep 28, 2011 at 10:46 AM, Jeremy Lumby <jlumby@mnvoip.com> wrote:
I am willing to help
Which item(s)? Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
All -----Original Message----- From: MICE Discuss [mailto:MICE-DISCUSS@LISTS.IPHOUSE.NET] On Behalf Of Jay Hanke Sent: Wednesday, September 28, 2011 10:56 AM To: MICE-DISCUSS@LISTS.IPHOUSE.NET Subject: Re: [MICE-DISCUSS] Akamai Cluster Help On Wed, Sep 28, 2011 at 10:46 AM, Jeremy Lumby <jlumby@mnvoip.com> wrote:
I am willing to help
Which item(s)? Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1 ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
I 'm available to help with any of the items >17:00CT the rest of the week... Or anytime Saturday, Sunday, or Next week (10/3 - 10/7) ~Matthew -----Original Message----- From: MICE Discuss [mailto:MICE-DISCUSS@LISTS.IPHOUSE.NET] On Behalf Of Jay Hanke Sent: Wednesday, September 28, 2011 9:37 AM To: MICE-DISCUSS@LISTS.IPHOUSE.NET Subject: [MICE-DISCUSS] Akamai Cluster Help We need volunteers for the following: -Install PDU and wire up server and switch power cords -Install Akamai router (not yet arrived) -Power up servers and do any remaining initial provisioning (After IP connectivity is established) -Akamai built in Route Servers Please reply to the list so everyone knows what's going on. Thanks, Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1 ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
I can help with those tasks, although if the servers are big know that I have puny arms. :-) What kind of plugs (volt/amp) do those PDUs need to be? I've got a couple 10 plug 110V/20A 1U horizontal units in need of a good home, but perhaps we want 208V. Jay: Do we have an ETA on that router? Anthony Anderberg Sr. Systems Analyst 320-234-5239 anthonyanderberg@nu-telecom.net www.nutelecom.net -----Original Message----- From: MICE Discuss [mailto:MICE-DISCUSS@LISTS.IPHOUSE.NET] On Behalf Of Jay Hanke Sent: Wednesday, September 28, 2011 9:37 AM To: MICE-DISCUSS@LISTS.IPHOUSE.NET Subject: [MICE-DISCUSS] Akamai Cluster Help We need volunteers for the following: -Install PDU and wire up server and switch power cords -Install Akamai router (not yet arrived) -Power up servers and do any remaining initial provisioning (After IP connectivity is established) -Akamai built in Route Servers Please reply to the list so everyone knows what's going on. Thanks, Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1 ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
What kind of plugs (volt/amp) do those PDUs need to be? I've got a couple 10 plug 110V/20A 1U horizontal units in need of a good home, but perhaps we want 208V.
I've got all the servers in the rack and cabled to the switches. All the servers are 110 VAC so those would work great. What kind of plug is on the cord? Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
Plug is NEMA 5-20P, the receptacles are NEMA 5-20R with the T-shaped neutral that can take 15A or 20A cords. Just to be sure - ten receptacles are enough? Anthony Anderberg Sr. Systems Analyst 320-234-5239 anthonyanderberg@nu-telecom.net www.nutelecom.net -----Original Message----- From: MICE Discuss [mailto:MICE-DISCUSS@LISTS.IPHOUSE.NET] On Behalf Of Jay Hanke Sent: Wednesday, September 28, 2011 3:54 PM To: MICE-DISCUSS@LISTS.IPHOUSE.NET Subject: Re: [MICE-DISCUSS] Akamai Cluster Help
What kind of plugs (volt/amp) do those PDUs need to be? I've got a couple 10 plug 110V/20A 1U horizontal units in need of a good home, but perhaps we want 208V.
I've got all the servers in the rack and cabled to the switches. All the servers are 110 VAC so those would work great. What kind of plug is on the cord? Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1 ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On Wed, Sep 28, 2011 at 4:28 PM, Anthony Anderberg <anthonyanderberg@nu-telecom.net> wrote:
Plug is NEMA 5-20P, the receptacles are NEMA 5-20R with the T-shaped neutral that can take 15A or 20A cords.
Just to be sure - ten receptacles are enough?
We would need two of them. 10 Servers, 2 switches, 1 (or 2) router (13 so far) ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
If the servers are using NEMA 5-20P plugs (20A), we should make sure that we are not overloading any of the PDUs based on the number of servers and their actual load. 20P plugs are one horizontal and one vertical. If they have two vertical prongs, then they are NEMA 5-15P plugs which are much more likely on servers that are not drawing very high amperages. Owen On Sep 28, 2011, at 2:28 PM, Anthony Anderberg wrote:
Plug is NEMA 5-20P, the receptacles are NEMA 5-20R with the T-shaped neutral that can take 15A or 20A cords.
Just to be sure - ten receptacles are enough?
Anthony Anderberg Sr. Systems Analyst 320-234-5239 anthonyanderberg@nu-telecom.net www.nutelecom.net
-----Original Message----- From: MICE Discuss [mailto:MICE-DISCUSS@LISTS.IPHOUSE.NET] On Behalf Of Jay Hanke Sent: Wednesday, September 28, 2011 3:54 PM To: MICE-DISCUSS@LISTS.IPHOUSE.NET Subject: Re: [MICE-DISCUSS] Akamai Cluster Help
What kind of plugs (volt/amp) do those PDUs need to be? I've got a couple 10 plug 110V/20A 1U horizontal units in need of a good home, but perhaps we want 208V.
I've got all the servers in the rack and cabled to the switches.
All the servers are 110 VAC so those would work great. What kind of plug is on the cord?
Jay
########################################################################
To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
########################################################################
To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
20P plugs are one horizontal and one vertical. If they have two vertical prongs, then they are NEMA 5-15P plugs which are much more likely on servers that are not drawing very high amperages.
The servers are all 5-15P. The outlet above the rack is a 20A twist lock so we'll need an adapter. Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On 9/28/11 5:45 PM, "Jay Hanke" <jayhanke@MANKATONETWORKS.NET> wrote:
20P plugs are one horizontal and one vertical. If they have two vertical prongs, then they are NEMA 5-15P plugs which are much more likely on servers that are not drawing very high amperages.
The servers are all 5-15P. The outlet above the rack is a 20A twist lock so we'll need an adapter.
Jay
Folks, We'd prefer that none of our equipment be modified without consultation of our deployment engineer responsible for this deployment. I'm sure that we'll be able to accommodate whatever environment that we need to and rapidly. Best, -M< ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On Sep 28, 2011, at 2:48 PM, Hannigan, Martin wrote:
On 9/28/11 5:45 PM, "Jay Hanke" <jayhanke@MANKATONETWORKS.NET> wrote:
20P plugs are one horizontal and one vertical. If they have two vertical prongs, then they are NEMA 5-15P plugs which are much more likely on servers that are not drawing very high amperages.
The servers are all 5-15P. The outlet above the rack is a 20A twist lock so we'll need an adapter.
Jay
Folks,
We'd prefer that none of our equipment be modified without consultation of our deployment engineer responsible for this deployment. I'm sure that we'll be able to accommodate whatever environment that we need to and rapidly.
Best,
-M<
I don't think anyone said anything about modifying your equipment, Marty. Ideally, the PDUs that provide the NEMA 5-20R or 5-15R receptacles in the rack should have the NEMA L5-20P on their input cord. Then, all that remains is to make sure that the total load being connected to each PDU does not exceed 18A max or 15A continuous. (You should always run a circuit with 25% continuous headroom and 10% max draw headroom in order to allow for line losses, etc.). Owen ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On Wed, 2011-09-28 at 14:56 -0700, Owen DeLong wrote:
Ideally, the PDUs that provide the NEMA 5-20R or 5-15R receptacles in the rack should have the NEMA L5-20P on their input cord.
If a new PDU needs to be purchased anyway... I suspect the Akamai servers have IEC inputs. It might be worth considering a PDU with IEC connectors on the output side. This could provide enough outputs in 1U vs needing 2U for two PDUs. Disclaimer: I haven't seen the rack, so this is just a general comment to consider. Richard ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
Disclaimer: I haven't seen the rack, so this is just a general comment to consider.
Since nobody follows my twitter feed... http://mankatonetworks.com/wordpress/?p=161 ;) ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On Sep 28, 2011, at 3:23 PM, Richard Laager wrote:
On Wed, 2011-09-28 at 14:56 -0700, Owen DeLong wrote:
Ideally, the PDUs that provide the NEMA 5-20R or 5-15R receptacles in the rack should have the NEMA L5-20P on their input cord.
If a new PDU needs to be purchased anyway...
I suspect the Akamai servers have IEC inputs. It might be worth considering a PDU with IEC connectors on the output side. This could provide enough outputs in 1U vs needing 2U for two PDUs.
If you do this, make sure you mount the strain reliefs on the PDUs and cable-tie the IEC plugs into the sockets. My experience with IEC PDUs has been generally positive, so long as you do this. If you don't, you are just asking for power issues as cables fall out (or partially out) of the PDUs. Owen ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
We'd prefer that none of our equipment be modified without consultation of our deployment engineer responsible for this deployment. I'm sure that we'll be able to accommodate whatever environment that we need to and rapidly.
I put in an email to him this morning, just haven't heard back yet. Jay ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1
On 9/28/11 6:02 PM, "Jay Hanke" <jayhanke@MANKATONETWORKS.NET> wrote:
We'd prefer that none of our equipment be modified without consultation of our deployment engineer responsible for this deployment. I'm sure that we'll be able to accommodate whatever environment that we need to and rapidly.
I put in an email to him this morning, just haven't heard back yet.
Thanks, I sent along the thread for him to take a look and prompted him to respond. If we need to modify the strips or anything of ours facing the infrastructure we would appreciate a heads up. Our documentation is fairly meticulous and we like to keep as-builts. We're well aware of all of the requirements to occupy all sorts of datacenters globally and will be happy to support the most cost effective implementation possible. I don't think that we're too far off from turning up. I'll be posting an "on" notice as soon as we get cleared from deployment. Best, -M< ######################################################################## To unsubscribe from the MICE-DISCUSS list, click the following link: http://lists.iphouse.net/cgi-bin/wa?SUBED1=MICE-DISCUSS&A=1